OK. That makes the Eaton breakers more attractive, but now that I have looked at their data sheet, I’m not sure. At 900% of their rating, they will trip in .003 to 3 seconds.
But I’m still wondering what guidelines need to be considered when selecting circuit protection. Theoretically, a short circuit will result in infinite amps, so maybe I should be looking at the high end of the time-current charts. If so, (at 10 times their rating) the Eaton thermal-magnetics will trip in .003 to .015 seconds, a slow magnetic-hydraulic in .010 to .3 seconds, a fast magnetic-hydraulic in .010 to .09, a thermal in .12 to .7 seconds and a mini fuse in .01 seconds.